What is the maximum overcurrent protective device allowed on a 480 volt branch circuit with several small motors connected all of which are under 1 HP and the maximum load of each motor is 5 amps?

Prepare for the New York City Electrician Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

Multiple Choice

What is the maximum overcurrent protective device allowed on a 480 volt branch circuit with several small motors connected all of which are under 1 HP and the maximum load of each motor is 5 amps?

Explanation:
Protect motor branches by sizing the short-circuit/ground-fault protection to up to 250% of the motor’s full-load current. If each motor can draw up to 5 A at full load, 250% of that is 12.5 A. The nearest standard protective device rating is 15 A, so the maximum allowed on the branch circuit is 15 A. Using 10 A would be undersized for motor starting currents, while 20 or 30 A would exceed the 250% limit. This sizing applies even with several small motors on the same branch, because the protection is based on each motor’s full-load current, not the total sum of all motors.

Protect motor branches by sizing the short-circuit/ground-fault protection to up to 250% of the motor’s full-load current. If each motor can draw up to 5 A at full load, 250% of that is 12.5 A. The nearest standard protective device rating is 15 A, so the maximum allowed on the branch circuit is 15 A. Using 10 A would be undersized for motor starting currents, while 20 or 30 A would exceed the 250% limit. This sizing applies even with several small motors on the same branch, because the protection is based on each motor’s full-load current, not the total sum of all motors.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy